SEGMENTO RF
Hello KNX community, I have a problem with ETS6.02v and the KNX RF/TP COUPLE 673 SECURE.
I create a Main Line L1 TP, in it I have created two line segments, Segment 1 L1 TP and Segment 2 L1RF.
In segment 2 L1 RF, it does not let me link the following KNX RF/TP COUPLE 673 SECURE device. Indicates that the device is not compatible with the line segment, this segment is configured as RF line.
However, it allows to link the KNX RF/TP COUPLE 673 SECURE in a new main L2 RF line.
What will be the problem of the error. Thanks.
-
Dear Mauricio
We have the same problem in a big project that was designed with RF segments.
Despite the fact that ets6 supports segments, it has not yet been implemented by the manufacturers and their product files. Therefore it is not yet possible to import these devices in segments.I would kindly ask you to also submit this to weinzierl so that they can see that several integrators need this asap...
Kind regards
Davy De Maegt
1 -
Hello Davy DeMaegt
I emailed them, the following is Weinzierl's response." Currently you can only use the coupler in the full RF line.
The function for the RF line as part of a TP line is not possible.
Unfortunately the Tools from KNX Association (Manufacturer Tool) are still missing this function.Thus, we cannot support this yet.
For comments or questions do not hesitate to contact me "Kind regards
0 -
Hello Mauricio, allow me to say that this
Unfortunately the Tools from KNX Association (Manufacturer Tool) are still missing this function.
is not correct. The Manufacturer Tool 6 that has been available to the manufacturers does allows to create products that support Security Proxy as well as Segment Coupler. Apparently Weinzierl wants to say something else, which I do not currently understand. I will however clarify this for you.
Regards, Vassilios