ETS 6.4 shows a nonexistent device in Programming Mode

Commenti

3 commenti

Accedi per aggiungere un commento.

  • Alexander Volle

    Hi there

    I've had this issue before when another device was in programming mode beforehand, and then I selected the new device for download without it being in programming mode. This then downloaded the new address to the existing device. I also got the topology warning, since the device  that was in programming mode was on a different line than addressed.

     

    What happens if you try to read out "Device Info" from the address? Does it show a different serial number? Can you gather which address it should have based on the linked group addresses and product type? You can then set the old individual address for that existing device.

     

    You can then connect the new device again, and put it into programming mode, "Download" all, and all should be well. If it doesn't work, you can try to download by serial number.

     

    You say you disconnected the KNX bus, but which line did you disconnect? Just the backbone, or just the subline. Or both?

    0
  • Luc Lanners

    Thank you all for your reply so far.

    I’ll try to describe the topology in a bit more detail.

    I have a main line (1.0 TP) with only one additional line connected to it, namely line 1.1, as shown in Screenshot 1. All devices are located on line 1.1.

    However, there is currently no device with the individual address 1.1.52 defined in the topology (see Screenshot 2).

    When I search for devices in programming mode in ETS, a device with the address 1.1.52 is still detected. This device is neither defined in ETS or the topology, nor is there actually any device with the address 1.1.52 connected to the bus (see Screenshot 3).

    I then performed an Individual Address Check, but no device with the address 1.1.52 was found either (see Screenshot 4).

    I really can’t figure out where this phantom device is coming from. Does anyone have any idea why this might be happening or how I can find out where ETS is getting this address from?

    Thanks in advance for your help!

    0
  • Alexander Volle

    You should perform a line scan in "Monitors". By doing this you can see if there are any devices missing. If there is one device missing in the line scan, then that device might have become the mysterious device 1.1.52. You should also see that 1.1.52 shows up as an "extra" device. 

     

    You can then check "Device Info" to see if the 1.1.52 device matches the missing device from the line scan.