Thermal valve won't close even when it's set to 0%

Opmerkingen

3 opmerkingen

U moet u aanmelden om een opmerking te plaatsen.

  • Torstein Christensen

    Hi

    Haw you disabled the "easy mounting"?

    Haw you track on NO/NC?

    0
  • Michiel Kenis

    Hi Torstein, 

    Thanks for reaching out. I'm unsure on what settings you are aiming for. 

    Where do I find these settings to change, and what does it imply? 

    Best, 
    Michiel

    0
  • Torstein Christensen

    The terminal valve on your picture is delivered in a "beetvin" state not open/not closed. After mounting you need to activate by energize it for approx. 5 min. Some actuators have a setting for this but you can just manually activate power. 

    NO/NC is the water flowing if it is energized or not hear you got a possibility to invert most actuators.

    Have it ever worked? 

    0