ETS 6.4 shows a nonexistent device in Programming Mode

Opmerkingen

1 opmerking

U moet u aanmelden om een opmerking te plaatsen.

  • Alexander Volle

    Hi there

    I've had this issue before when another device was in programming mode beforehand, and then I selected the new device for download without it being in programming mode. This then downloaded the new address to the existing device. I also got the topology warning, since the device  that was in programming mode was on a different line than addressed.

     

    What happens if you try to read out "Device Info" from the address? Does it show a different serial number? Can you gather which address it should have based on the linked group addresses and product type? You can then set the old individual address for that existing device.

     

    You can then connect the new device again, and put it into programming mode, "Download" all, and all should be well. If it doesn't work, you can try to download by serial number.

     

    You say you disconnected the KNX bus, but which line did you disconnect? Just the backbone, or just the subline. Or both?