WAGO GATE 753-646 ETS

Kommentarer

1 kommentar

  • Avatar
    Pierre FLOT

    Hello

    What PLC do you have ?

    Have you see the wago app note and did you try the example that you can found on the wago's web site ?

    First : 

    You need to do your PLC program

    Generate a Symbol file in Codesys to Export variable to KNX

    In ETS, open the device plugin of the 753-646, and import your file.

    You can now link object and GA.

    Dont forget to set Send on Reset/Read on Reset and flag's if necessary

    In ETS Download Application of the 753-646

    In codesys, you can see the state of KNX Master function block, if not OK, do a reset from the Codesys menu then select start.

     

     

     