WAGO GATE 753-646 ETS
Hello i have problem with my device to connect PLC and KNX bus. First of all it don't work correct because it still is not in device mode. In ETS i made project and i cannot unprogramm this device cause it popping error "T_ack didn't get on telegram" ( i don't really know what it means). I tried to make new project and program this device on diffrent adress, but the previous project block it. Do you have any suggestions what i supposed to do?
-
Hello
What PLC do you have ?
Have you see the wago app note and did you try the example that you can found on the wago's web site ?
First :
You need to do your PLC program
Generate a Symbol file in Codesys to Export variable to KNX
In ETS, open the device plugin of the 753-646, and import your file.
You can now link object and GA.
Dont forget to set Send on Reset/Read on Reset and flag's if necessary
In ETS Download Application of the 753-646
In codesys, you can see the state of KNX Master function block, if not OK, do a reset from the Codesys menu then select start.